3/24/2010 1:47 AM | |
Joined: 10/7/2005 Last visit: 11/11/2024 Posts: 3026 Rating: (1057)
|
Hello BGreen It most definetely does. The "limit" of 244 Bytes of cyclic I/O's per Profibus Slaveis a Profibus system "limit" and independent of the manufacturer. While 244 Bytes of cyclic I/O's per DP Slave areusually enough, you can get more data from a DP Slave via acyclic comms ifDPV1 is supported by the DP Master (don't know if the TI DP Master card supports DPV1) as well as the DP Slave (Sinamics are DPV1 capable). I hope this helps |
Cheers |
|
3/24/2010 12:02 PM | |
Posts: 510 Rating: (119)
|
The SIMATIC 505 family does not support DPV1 billwest |
This contribution was helpful to1 thankful Users |