Hi, I'm not sure of what you want to do as your post is very confusing. Normally EM modules is for S7-200 PLC. Step-7 5.5 is different software from V10.5 and so examples are not the same. Also please keep in mind that you can only program S7-1200 controller with version 10.5. If you want to use it for S7-300/400 controllers you need to upgrade to v11. In any case upgrade to V11 is adviced. Now I don't know about what diagnostics you speak, but you could check option when diagnostics are done via integrated WEB server on the CPU. If your CPU is S7-1200 then its good idea. How do you display the diagnostics buffer of a SIMATIC CPU with integrated web server on a SIMATIC Panel? If you're working on S7-300/400 PLC you could use S_ALARM messages for displaying the diagnostics. Also, Comfort series panels has lots of options for diagnostics. So maybe come back here with more infor on your application |
Best regards, |
|
5/16/2012 10:34 PM | |
Joined: 7/7/2010 Last visit: 7/16/2024 Posts: 14954 Rating:
|
Those FBs you see in the manual are only available in the V11 (Basic & Pro) version of the Portal. In the OB (diagnostic error routine), you may notice the OB #'s for the diag routine are different depending on theversion of the software used and the PLC firmware in the project. If you create a diag OB, the portal will assign the correct number for you automatically. Let it. There is a thread on how to do the diagnostics written some time ago. Scroll to the bottom to download screenshots: /tf/WW/en/Posts/34983 |
science guy |
|
This contribution was helpful to