7/25/2011 9:49 AM | |
Posts: 3 Rating:
|
Details: Is it possible to establish communication between CPU 414-4H and CPU412-3H system directly via profibus. where the profibus port of one 414-4H system CPU is connected to the profibus port of 412-3H CPU via profibus?? Do we need any CP 443-5 Ext or we can directly use the DP ports of the CPUs? Please help on an urgent basis..I am attaching the Automation Configuration. Attachmentautomation configuration_limestone handling.pdf (126 Downloads) |
7/25/2011 6:32 PM | |
Posts: 947 Rating:
|
If you run netpro and try make connection by profibus, Then you see - this impossible |
7/27/2011 10:22 AM | |
Joined: 12/22/2006 Last visit: 1/25/2022 Posts: 1742 Rating:
|
Hello, Have a look to the manual: http://support.automation.siemens.com/WW/view/en/1186523 Chapter 11 of that manual describes the communication for a H-system. Annex E shows youthe supported CPs. For the number of CPs andfurther HW needed,you will have to decide if you want to have the communication fault-tolerant or not, how far you want the redundandancy to reach. You require a suitable CP for fault-tolerant S7 connections via PROFIBUS. These connections are not possible via the internal PROFIBUS-DP interface. (p.168 of the manual). |
Last edited by: jklm at: 7/27/2011 10:23 AMBest regards |
|
7/29/2011 8:31 AM | |
Posts: 3 Rating:
|
Hello, Thank you. The manual is also very helpful.
|