3/27/2019 6:15 AM | |
Joined: 1/1/2017 Last visit: 7/22/2024 Posts: 331 Rating: (11) |
Hello Sid, When you are selecting 400-F CPU it's only allowed to mount it on either UR-2 ALU RACK or CR ALU Rack only. Reason behind this is that these racks are specially manufactured to get adjusted with any sort of S7 400 series PLC's. UR-2 normal rack is only for mounting normal standalone S7 400 series CPU's along with other peripheral devices like IO modules, CP cards, etc. F CPU's are special type of CPU's for special applications where process dependancy is at topmost priority & no sort of external faults can cause the process to withhold. That's why F-series CPU's are used in those sort of applications. Also you can search the topic in web giving the MLFB of the CPU & refer the datasheet of that CPU also. Refer this link: https://support.industry.siemens.com/tf/ww/en/posts/ur2-rack-for-s7-400h/147075?page=1&pageSize=10 Regards OmKris AttachmentF_System_Requisites.pdf (538 Downloads) |
This contribution was helpful to2 thankful Users |
Follow us on