7/3/2009 12:08 PM | |
Joined: 3/21/2006 Last visit: 7/26/2024 Posts: 10228 Rating: (1181) |
Hello, Isn't be possible to connect via How can you connect an operator panel directly to an H system without using repeaters? About diagnostic repeaters I don't know. I think this kind of connection isn't recommended. And probably if you already tried without success...(of course if hardware is connected according instructions) Regards Hristo Mihalev |
This contribution was helpful to1 thankful Users |
7/5/2009 8:50 PM | |
Joined: 12/22/2006 Last visit: 1/25/2022 Posts: 1742 Rating: (308) |
Hello, I guess that you refer to point 4 of this FAQ: http://support.automation.siemens.com/WW/view/en/22584322 where two repeaters are used (but only one is powered, depending on the active CPU). I don't see a reason why this would not work with two diagnostic repeaters. A possible setup i belive that could work, is as follows: Connect each CPU to the segmentDP1, with DP1 terminated. And connect the TP to both segment DP2 of the repeaters. And power only one repeater. But I agree with the comment that you could try without repeater at all as suggested. |
Best regards |
|
Follow us on