Hello, When you do not have the original project, perhaps you can try the following: Thanks to Ayman Elotaify
Best regards, Wizard
|
Last edited by: Wizard at: 05/20/2022 11:05:48 |
|
This contribution was helpful to1 thankful Users |
5/23/2022 8:44 AM | |
Joined: 8/3/2009 Last visit: 11/15/2024 Posts: 14176 Rating: (1774)
|
Hello you can use also only the User Administration of the new Dummy Project: -> Create a new dummy project, edit the PW for the Admin user -> Generate the Project in TIA Portal -> look in the generated files (IM Folder-> then downwards in the folders) -> there is a PDATA.pwx file -> copy this file to a USB Device or SD Card and connect on the Panel -> Open the File explorer on the Panel -> copy the PDATA.pwx file to the Flash/Simatic Folder and overwrite if there is an existing one -> Restart the Runtime on the Panel then the Pwx file will be imported and overwrites the existing User Administration But of course reloadiing the original Project from TIA Portal with overwriting User Administration would be the better solution but if you do not have it, this "emergency way" should work and makes your admin user work again (in most cases) Bye Murof |