Joined: 8/11/2018 Last visit: 6/17/2022 Posts: 21 Rating: (0) |
Thank you for your sample, but I need transfert analogic input for LOGO to S7-1200 (I need transfret word but your sample transfert only byte and LOGO don't whant sent more long byte). Can you say me the solution to transfert word from AI? Thank you ------------------------------------------------------------------------------------------ |
Last edited by: Jen_Moderator at: 03/23/2020 06:08:44New subject after splitting |
|
3/21/2020 5:45 AM | |
Joined: 12/18/2014 Last visit: 11/7/2024 Posts: 34158 Rating: (4254)
|
Who is client and who is server? |
3/21/2020 4:02 PM | |
Joined: 12/18/2014 Last visit: 11/7/2024 Posts: 34158 Rating: (4254)
|
Here's a example with one S7-1212C (TIA V13 SP2) and two LOGO!s 0BA8.Standard (LSC V8.0). The LOGO!s are the clients, the S7 is the server for both. AttachmentS7-1212C with 2 LOGO! 0BA8.zip (360 Downloads) |
3/23/2020 4:49 AM | |
Joined: 12/18/2014 Last visit: 11/7/2024 Posts: 34158 Rating: (4254)
|
I upgraded the TIA project to V15.1 and your CPU. I had adapted the LOGO! network project. It now contains a LOGO! 0BA8.Standard and a LOGO! 8.FS4. AttachmentS7-1212C with 2 LOGO! 0BA8_V2.zip (291 Downloads) |