11/5/2020 12:21 AM | |
Joined: 4/21/2020 Last visit: 10/2/2021 Posts: 1 Rating: (0) |
Hi Denilson, Do you have a sample project like this in version TIA Portal V15.1? Also, I am having trouble seeing my load cell output. I am trying to read it as a Int and my result is not changing. Thoughts? Thank you. ------------------------------------------------------------------------------------------ |
Last edited by: Jen_Moderator at: 11/05/2020 11:05:05New subject after splitting |
|
11/5/2020 6:13 PM | |
Joined: 7/7/2010 Last visit: 7/16/2024 Posts: 14965 Rating: (2393)
|
When you see yellow in the plc tag editor, your tags have overlapping memory. Also, I think you meant INT, not DINT. I believe the load cell AI will read as an INT, not a DINT. That's 2 bytes, not 4. Avoid using the same bytes for multiple tags unless you know exactly what you are doing and why.
|
science guy |
|