Can I use 2 Active line modules (ALM) (booksize format ) in parallel (AC and DC)? pls help me! ths |
7/5/2011 4:30 PM | |
Posts: 133 Rating: (13) |
There is no paralleling of any booksize S120 Line Modules, Motor Modules, or AIM units at this time. |
Last edited by: Drives_Coach at: 7/6/2011 6:14 PM |
|
7/6/2011 2:43 AM | |
Posts: 344 Rating: (50)
|
It is not possible to connect S120 Booksize and Blocksize units in parallel. It is possible to connect chassis S120 units in parallel. Attached section of the Sinamics engineering manual describes parallel chassis unit operation. AttachmentSinamicsParallelConnection.pdf (354 Downloads) |