3/6/2024 3:18 PM | |
Posts: 13 Rating:
|
Hello everyone, I'm trying to set up a Modbus connection between a LOGO! 8.3 and a Unified Basic Panel, however, I am unable to get the connection working. I'm wondering if I'm missing anything on either side. I include screen captures on both LOGO's and screen's end. P.S. - I have done VM mapping for LOGO! just not on the network connections, is that necessary? Thank you for your time AttachmentCaptures.zip (516 Downloads) |
3/6/2024 5:24 PM | |
Posts: 13 Rating:
|
I'll try it and update the post with relevant information. |
3/14/2024 9:20 AM | |
Joined: 8/3/2009 Last visit: 9/16/2025 Posts: 16436 Rating:
|
Hello Yes I tested it a long time ago and there was only the RTU document available, now there is also a TCP one: https://support.industry.siemens.com/cs/ww/en/view/109925839/177165909131 I did the test again with a Unified Comfort 1000 and a Unified Basic Panel. I activated the Modbus TCP Server in the LOGO and just write some digital inputs to the VM area to do a quick test (I´m no LOGO Professional). I tested the Registers V und VM in the LOGO addressed with 0x1-0x16 and with 4×400001 (Word/ +-Int) in Unified. In Simulation and on real Panel Runtime I get a connection and I could also see the value change if I used the simulation board on the LOGO, so the connection works. I noticed a byteswap in VM addressing and the LOGO seems to be able to handle only one HMI connection. If a second one at the same time could not be connected. I know this is only a rudimantary test scenario but I hope this helps if someone want to do this kind of communication. Bye Murof |
Last edited by: Murof at: 03/15/2024 08:49:21If this Information really helps, you could use the Rate function |
|