Techno_Taru, The following is not true: "Note: CFC will be created under OB35 Cyclic interrupt (100ms) for execution." The CFC program can be executed in OB3x range like OB32, 33, 34, 35 etc. Those are interrupt OB's which basically means consistent execution of the program. If you put blocks in OB32 (for example 1 sec.), the program will make sure all blocks are executed in the 1 second cycle, unlike OB1 where the execution time can take longer depending on how large the program is. The same applies for the hardware signals which can be put in a PIP (Process Image Partition) and can also be mapped to a specific execution time. PS: APL blocks are not executed properly when they are not called in OB3x. PS2: PCS7 Cemat differs, where blocks are put in OB1.
|