9/6/2020 12:14 PM | |
Joined: 12/16/2018 Last visit: 6/16/2024 Posts: 67 Rating: (0) |
Hi I have installed Pcs7 v8.0 SP2 with PCS7 AP Library V8.0 on the windows 7 Ultimate SP1 32bit. Does anyone have a solution? AttachmentAttachment.zip (61 Downloads) |
9/7/2020 7:49 AM | |
Joined: 5/3/2017 Last visit: 5/21/2024 Posts: 673 Rating: (217) |
Hi DPCS, can you explain me for what and why you want to use the inputs OpenMan and CloseMan in CFC? The philosophy of the APL-blocks is that
If in some situations the valve has to be closed/open regardless of the operating mode (automatic / manual) then you can use the inputs OpenForce and CloseForce to close or open the valve. For more information see the manual PCS 7 Advanced Process Library at the sections Forcing operating modes and VlvL I/Os. With regards |
Last edited by: Heisenberg2 at: 09/07/2020 07:49:58 |
|