4/4/2011 1:25 PM | |
Posts: 4 Rating: (0) |
Hi all I want to ask if i can use the Y-link with 2 S7-300 CPU to use this configration as a redandancy system |
4/4/2011 5:08 PM | |
Posts: 947 Rating: (45) |
In manual wrote: Y-Link work only with H-CPU |
Last edited by: gre_m at: 4/4/2011 5:09 PM |
|
4/6/2011 5:01 AM | |
Joined: 10/7/2005 Last visit: 12/24/2024 Posts: 3029 Rating: (1058)
|
Hello eng.mustafa.hussein1 as it is not 100%clear what you want to do here is what's possible for each case: 1.) S7 300 Software redundant system as the redundant DP Master system: You can NOT connect aY-link to it. 2.) S7400 HSystem as the redundant DP Master system: You can (of course) connect aY-link to itand can connectDP Slaves to the Y-Linksunderlying non-redundant Profibus including S7 CPU's as so called "I-Slaves" (intelligent DP Slaves) and the links below have more on this: How is the Y link structured? Configuring an S7 CPU as DP slave on the H system using a Y-Link I hope this helps |
Cheers |
|
This contribution was helpful to1 thankful Users |
4/7/2011 3:04 PM | |
Posts: 947 Rating: (45) |
3xx CPU can connect to Y-link as slave. Y-link in this caseis master for cpu 3xx. But needed 400H as master for Y-Link |
4/7/2011 6:16 PM | |
Joined: 9/27/2006 Last visit: 12/26/2024 Posts: 12316 Rating: (2695)
|
[
Hello all; All S7-CPUs (with integrated Profibus interface) can be inserted as DP-slaves to a 3rd-party DP master using their specific gsd file. The following FAQ showswhere to locate these gsd files: Where can I procure the GSD files for my S7-300 CPUs? Hope this helps, Daniel Chartier |
This contribution was helpful to1 thankful Users |
10/21/2014 11:49 AM | |
Joined: 9/3/2014 Last visit: 3/13/2019 Posts: 4766 Rating: (122) |
|