Hello rouk! Please see the help of the APL. In the topic "Manual and automatic mode for control blocks" I have found this information: Switchover from automatic mode to manual mode
When changing over from "automatic mode" to "manual mode", the last valid control settings (Manipiulated Value Switchover from automatic mode to manual mode
The switchover from manual to automatic mode can take place with or without the internal setpoint tracking the process value. You specify this behavior on the Switchover with internal setpoint tracking process variable (
|
Greetings |
|
This contribution was helpful to1 thankful Users |
6/9/2015 2:15 PM | |
Posts: 36 Rating: (1) |
I use SP_TrkPV and it works , thanks Jules Stoh |