Joined: 10/9/2021 Last visit: 10/7/2024 Posts: 20 Rating: (0) |
Hello All, I am working on a project with PCS7 V9.1 I have following configuration 1. ES-OS 2. OS I wish to create redundancy between two. I configured everything as written in document "PCS 7 Minimal Configurations". When i download my project to standby OS, i do not get complete project data such as user defined process pictures, user-administration data and so. When I activate runtime on Standby OS, the runtime graphics seems completely different than master OS. What could the reason? Its bit urgent. Thank you in advance. ------------------------------------------------------------------------------------------ |
Last edited by: Jen_Moderator at: 02/25/2022 09:24:18New subject after splitting |
|
2/25/2022 8:01 AM | |
Joined: 5/3/2017 Last visit: 5/21/2024 Posts: 673 Rating: (217) |
Hi Shree2893, I have look at the application example PCS 7 Minimal Configurations and I have found the problem. In the document is one step not described and that is the step where you have to configure the on the OS-Master Server who is the OS-Standby Server, for more information see the PCS 7 Compendium Part A - Configuration Guidelines at section OS server. I pretty sure that you miss that step. If you want to configure your system I recommend to you the PCS 7 Compendium Part A - Configuration Guidelines. In this document you can find all steps that are need for the configuration of your PCS 7 system. With regards |