You see in the attched picture that i habe interconnected the Ramp_SPExt block but why I don't see it in the List editor? |
4/11/2024 4:46 AM | |
Joined: 3/14/2008 Last visit: 9/17/2024 Posts: 2095 Rating: (936)
|
Hi, My experience is that the "Interconnection to" column only shows interconnections between technological I/O (green background). The "Reference block variable" column should list connections to blocks with normal I/O. |
If I could help you, you can use the RATE button. Thank you. |
|
This contribution was helpful to1 thankful Users |