Hello, As far as I know, communication between 2 CPUs that are capable of executing of S7F/FH system blocks is possible that are mainly H-CPU. Communication from F-CPUs,distributed Safety optional package, and F/FH systems is also possible.The different options are discussed in chapter 3 of "Industrie Software Safety Engineering in SIMATIC S7" manual.So, you can not create such a safety function to link your standard communication in a standard CPU to those safety optional package. I hope this helps, Hamid Hosseini |