6/20/2009 9:06 AM | |
Posts: 3 Rating: (0) |
HOW CONFIGURATE WIN CC 7 WITH A 400H WITH A STANDARD ETHERNET PORT AND HAVE A REDUNDANCY ON THE COMUNICATION FORM PC TO 400H BY DOUBLE ETHERNET CARD? REGARDS. |
6/20/2009 9:22 AM | |
Joined: 3/18/2009 Last visit: 5/6/2024 Posts: 306 Rating: (94) |
400H ---> WinCC with standard ethernet port is not supported. You will need a CP1613 in your PC and redconnect liceneses. Have a look at thisthread. If you use two CP1613 you can form redundant communication link in netpro.
|
6/23/2009 7:56 AM | |
Joined: 9/1/2005 Last visit: 10/14/2024 Posts: 4109 Rating: (195) |
Thread closed, because question is already discussed in the thread with the subject CONNECTION BY DOUBLE ETHERNET LINE TO 400H. You can find it within the conference SIMATIC WinCC Best regards CS Moderator |