5/2/2018 11:13 AM | |
Joined: 9/21/2017 Last visit: 11/3/2021 Posts: 30 Rating: (1) |
It is possible? Via build in runtime, OPC-UA server ? |
5/2/2018 12:26 PM | |
Joined: 5/16/2014 Last visit: 9/12/2022 Posts: 7298 Rating: (2169)
|
Hello yos986, I may not really understand, what your question is. 1. If you log tags from an OPC-Server in the WinCC-Taglogging, and you use in the configuration for "Archiving" / "Acquisition type" the option "After every change", WinCC-Taglogging is using the timestamp which is send by the OPC-Server with the change of the value. 2. If you have a S7-PLC you can send the timestamp from the PLC by telegram, see FAQ "How do you use SFB37 (AR_SEND) for process-driven archiving of process values in WinCC Tag Logging archives?" https://support.industry.siemens.com/cs/ww/en/view/23629327 3. If 1 and 2 are not possible, you could write values and timestamps via C-script in the Taglogging-Archive by using the ODK-Function "TLGInsertArchivData". Regards Georg Berghof AttachmentTLGInsertArchivData.pdf (90 Downloads) |
PS: If this post did really help you, you may use the Rate-button |
|