8/21/2014 4:19 AM | |
Joined: 10/7/2005 Last visit: 5/3/2024 Posts: 3004 Rating: (1046)
|
Hello Sqruel no problems with using either OLM's and/or Repeaters behind a Y-Link (you can even usean OLM ring if you wish). The Y-Link forms a new independent DP Master systemand youcan set it's Profibusproperties independently (including specifying the number of OLM's and/or repeatersso that the bus timing iscalculated accordingly). The only thing you want to check before adding anotherDP Slave to your Y-Link is that you don't "break" its244 Byte I/O Limit. I hope this helps |
Cheers |
|
8/21/2014 7:42 AM | |
Posts: 6 Rating: (0) |
Thank you for your explanation. Silly question but how can I check if I'm not breaking the 244 byte limit? |
8/21/2014 7:58 AM | |
Joined: 10/7/2005 Last visit: 5/3/2024 Posts: 3004 Rating: (1046)
|
Hello Sqruel Option 1: Manually add up all Input Bytes and all output Bytesof all DP Slave behind the Y-Link and make sure the Sum of Inputs orthe Sum of Outputs does NOT exceed 244 Bytes. Option 2: Let Step 7 HWconfig do the job for you and do a test config (it'll pop up a warning shouldyou"break"the 244 ByteLimit) |
Cheers |
|
8/21/2014 8:33 AM | |
Posts: 6 Rating: (0) |
Thank you very much. |
This contribution was helpful to1 thankful Users |
Follow us on