4/12/2023 6:11 AM | |
Joined: 3/25/2008 Last visit: 5/21/2024 Posts: 187 Rating: (8) |
Hello you just need to rewrite the .txt extension to .dnl
Attachment9824-0729-91 02 2_11.txt (941 Downloads) |
4/13/2023 10:02 AM | |
Joined: 3/25/2008 Last visit: 5/21/2024 Posts: 187 Rating: (8) |
you will have to look at the control parameters and not at the P700 - which does not say anything |
4/17/2023 9:13 AM | |
Joined: 5/27/2022 Last visit: 8/27/2023 Posts: 6 Rating: (0) |
Today I had time to test the compressor with new parameters and the compressor doesn`t work. I got the fault "Compressor Motor Converter Timeout" I managed to download the original parameters from Micromaster, but they are slightly modified. On these parameters, the inverter starts, sets the minimum frequency and enters the error 'Compressor Motor Converter Timeout' or 'Compressor Motor Converter Format Fail 52' here it looks as if the elektronikon didn`t receive information that the inverter has reached the minimum frequency. I give my parameters, this is Starter export project
Attachment9824-0729-9102 minfreq.zip (634 Downloads) |
4/20/2023 6:08 AM | |
Joined: 3/25/2008 Last visit: 5/21/2024 Posts: 187 Rating: (8) |
it can not be opened |
4/21/2023 10:41 AM | |
Joined: 5/27/2022 Last visit: 8/27/2023 Posts: 6 Rating: (0) |
I don't know why. I upload all my Starter project folder Attachment9824-0729-9102 minfreq.zip (593 Downloads) |
4/24/2023 5:45 AM | |
Joined: 3/25/2008 Last visit: 5/21/2024 Posts: 187 Rating: (8) |
I don't see that you uploaded the backup I sent you there |
Follow us on