11/9/2021 9:22 PM | |
Joined: 10/14/2021 Last visit: 7/9/2024 Posts: 3 Rating: (0) |
Good evening ! I would like to appeal to the forum participants with a request to help correct the program! Logo! OBA6 12 / 24RC, Logosoft7, Automatic gate project, it is not possible to make protection: when the gate opens (or closes), an opposite blocking is required, when any of the buttons is touched, the gate must stop. Project details: Inputs: i1 open button, i2 close button, i3 limit switch open, i4 limit switch closed, i5 safety sensor, i6 additional stop button Outputs: Q1 gate relay open, Q2 barely close the gate, Q3 Safety light, Q4 buzzer , B009 forgot to close the gate - it will close itself. I ask if anyone has the opportunity to suggest how to correctly implement this blocking, please help me, I was tormented. Also welcome general configuration hints, I apologize for the translation, Thank you! Attachmentсхема ворот на форум.zip (516 Downloads) |
Last edited by: zigzac at: 11/09/2021 21:25:36Last edited by: zigzac at: 11/09/2021 21:27:04Last edited by: zigzac at: 11/09/2021 21:27:33Last edited by: zigzac at: 11/09/2021 21:42:18 |
|
11/10/2021 12:59 PM | |
Joined: 6/19/2019 Last visit: 7/10/2024 Posts: 697 Rating: (73) |
Hello zigzac, Here is your modified program when opening or closing gates and press any button it will stop, again short press it will move again also I modified your I5 signal when closing gates and safety sensor was trigered it will stop closing but then safety sensor not trigered after your time (2 s) it will start closing automaticaly AttachmentGate.zip (484 Downloads) |
This contribution was helpful to1 thankful Users |