10/2/2006 12:21 PM | |
Posts: 3 Rating: (0) |
hi, is it possible to change the drive-settings using a digital in? i want to switch between a 3kw drive and a 2.2 kw drive. thanks,pico |
10/2/2006 1:24 PM | |
Joined: 4/24/2006 Last visit: 10/28/2024 Posts: 8756 Rating: (1170) |
Hello, I think when you use BiCo, you can do it. Here is a manual: http://support.automation.siemens.com/WW/view/en/21741841 Chapter 3.13 and 3.14 will explain something. Best regards, Wizard |
10/18/2006 12:53 AM | |
Posts: 130 Rating: (1) |
Read up on parameter P0810 and P0811... let me know... |