1/6/2023 1:15 PM | |
Joined: 9/24/2019 Last visit: 11/15/2024 Posts: 2 Rating: (0) |
Hello, I recently had a similar problem. The problem appear after a power ON and those are the alarm we had. All my drive on a CX32 have the same fault. F1600 with number (9999) F1611 with number (2001) F30651 with number (7) The solution on fault 1611 is the text below Re fault value = 2000, 2001, 2002, 2004, 2005: - check the tolerance time SGE changeover and if required, increase the value (p9650/p9850, p9652/p9852). I have 7 module with the same value that are the following, but only one of them had a fault. Should I really try to increase the value and how much should I increase the value? 9650 = 500 ms, 9652 = 1s, 9850 = 500000 us, 9852 = 1000 ms. ------------------------------------------------------------------------------------------ |
Last edited by: PDauphinais at: 01/06/2023 13:18:16Last edited by: Jen_Moderator at: 01/09/2023 10:47:36New subject after splitting |
|
1/10/2023 3:03 PM | |
Joined: 10/11/2006 Last visit: 11/18/2024 Posts: 5941 Rating: (816)
|
Hello, |
With best regards, |
|