9/22/2016 9:36 PM | |
Posts: 5 Rating:
|
Hello, I'm developing my first project with LOGO! 24RC and I'm a little confused with data info at the datasheet. The datasheet says that digital input of LOGO! recognizes an input voltage as SIGNAL 1 if it is above 12VAC but it doesn't tell the voltage limit. May I use an input of 24VDC as signal 1? Is it possible to use a 127VAC as well? Thank you for your support. Silvino ------------------------------------------------------------------------------------------ |
Last edited by: Min_Moderator at: 9/23/2016 1:56:14 PMNew subject after splitting |
|
9/23/2016 2:53 PM | |
Joined: 12/18/2014 Last visit: 7/22/2024 Posts: 33386 Rating:
|
No, 127 VAC is not permissible for a digital input of the Logo. Permitted are: For AC: maximum 26.4V See also attachment. AttachmentLOGO! 8 Soft manual 0BA8 2014_06 pages 301-303.pdf (176 Downloads) |
This contribution was helpful to
1 thankful Users |
9/27/2016 6:46 AM | |
Joined: 12/18/2014 Last visit: 7/22/2024 Posts: 33386 Rating:
|
Hello KDiniva, you're welcome. Thanks for your Feedback. |
Follow us on