Hi All First I have searched too death and cant find a solution too my problem / inexperience My Logo Program works fine but will happily take any advice My problem is i am using 4 Analog Flags AM1 AM2 AM3 and AM4 too take an adjustable setpoint from the KTP400 On plc Restart these return too 0 I understand using the one shot output from flag M8 too set them would be the solution however any means I use too set these flags is persistent and then they are not adjustable from the HMI Attached is the Code Kind Regards Trev AttachmentRPC Heating.zip (205 Downloads) |
10/29/2018 6:51 PM | |
Joined: 12/18/2014 Last visit: 11/4/2024 Posts: 34140 Rating: (4254)
|
No, no, I had written I had solved the issue with a word of VM memory. You replace your analog marker with an analog network input with a free word address from the VM area.Both in the LOGO! as well as in WinCC. AttachmentStoring_Setpoint_from_HMI_Fail-safe_in_LOGO!_with_zero_setting_(automatically)_FS4.zip (305 Downloads) |