12/3/2019 2:44 PM | |
Joined: 2/22/2008 Last visit: 8/6/2024 Posts: 2698 Rating: (208) |
You can try out something like the example in the attachment. The arithmetic block will store the last output value Aq from pi controller, when automatic is switched off (check last value in parameter). The following trigger is only for recursion back to pi controller. Regards, Scorp AttachmentPIMq1.zip (226 Downloads) |
12/4/2019 10:24 AM | |
Joined: 12/18/2014 Last visit: 11/2/2024 Posts: 34129 Rating: (4250)
|
In attachment a possible solution to save the output value of the PI controller in the Mq parameter when switching off the automatic. AttachmentPI_controller_save_automatic_value_for_manual_value_FS4.zip (223 Downloads) |
12/5/2019 12:00 PM | |
Posts: 4 Rating: (0) |
problem solved, thanks for your help. |
Follow us on