Thanks should i have to set the cp1543-1 ip as"router address" on pn interface of all cpu? |
2/27/2023 8:00 AM | |
Joined: 1/21/2013 Last visit: 10/28/2024 Posts: 3218 Rating: (499)
|
Hi aleb2, No, you don't need to configure a router. This would only be necessary if the PLCs should also be able to access the network connected to the CP 1543-1. For example, if the PLCs need a connection to the Internet. In this case you would have to configure the IP address of your S7-1500 - the one equipped with the CP 1531-1 - as router address and you would have to activate IP forwarding on this PLC. Kind regards |
2/27/2023 10:09 AM | |
Joined: 1/21/2013 Last visit: 10/28/2024 Posts: 3218 Rating: (499)
|
Hi aleb2, Yes, you can download the PLC and HMI program to the CPUs and HMI devices. And you will also be able to monitor the program inside your CPUs. The only condition is that all routing devices - according to your description this will be only your S7-1500 - must support the "S7 Routing" function in S7 subnets. But you won't be able to perform operations that can't be routed, like searching for accessible devices in your machine network or assigning device names there. Kind regards |
Last edited by: Stefan Arcularius at: 02/27/2023 10:15:27Added link to FAQ |
|