Hi, Are you sure the MQTT block is working in your PLC? What is the status of this block? Kind regards |
6/6/2024 11:56 AM | |
Joined: 6/2/2024 Last visit: 6/10/2024 Posts: 6 Rating:
|
Until now, I had the status 8620, but now is something else, in 8601. |
6/6/2024 1:47 PM | |
Joined: 1/21/2013 Last visit: 7/19/2024 Posts: 3005 Rating:
|
Hi, Your screenshot shows an active error state for the function block. The meaning of error state 16#8601 is "Error in subordinate TCON statement". This means you need to look at diagnostics.subfunctionStatus and look for the value in the ERROR and STATUS parameter table. For more information on how to use the diagnostic data, refer to chapter 11.2 of the documentation provided with the Libraries for Communication. In principle, communication with the virtual machine should also work. However, you should verify this using common tools such as ping. Kind regards |
6/6/2024 6:43 PM | |
Joined: 6/2/2024 Last visit: 6/10/2024 Posts: 6 Rating:
|
Thank you for your answer. However, what IP's you suggest I ping? the one for the broker or some others? |