6/18/2008 8:47 PM | |
Posts: 7 Rating:
|
cok çalışman gerek |
6/20/2008 3:04 PM | |
Posts: 39 Rating:
|
Hello sakir Do you already know the FAQ for the torque limiting? There you find a description about the set up of torque limiting. http://support.automation.siemens.com/WW/view/en/22057029 - The settings “Load side” and “%” works with values related to the load side. In your case you must consider the formula for linear axis. You find the formula in the mentioned FAQ. - With the setting “Motor” can be entered the torque limit, without conversion, directly. - It is important that you set the reference torque (max. torque) of the motor in the configuration data “TypeOfAxis.SetPointDriverInfo.DriveData.maxTorque” (otherwise the evaluation does not fit). Regards ThomasD |
6/20/2008 3:58 PM | |
Posts: 3 Rating:
|
Dear ThomasD, Link not work |
6/20/2008 5:01 PM | |
Posts: 39 Rating:
|
Hello sakir You can find the information also in following document (chapter 1.5). http://support.automation.siemens.com/WW/view/en/27002093 Regards ThomasD |