Hi, well I am not sure, whether I got your problem... In the S7- CPU you will NOT find any downloaded CFC, just DBs, FBs,FCs.... so you can just upload e.g. parameters of a motorblock, but not the CFC chart in which this block may be located. http://support.automation.siemens.com/WW/view/en/335186 nemo |
8/10/2006 12:22 PM | |
Joined: 8/10/2006 Last visit: 7/15/2024 Posts: 156 Rating: (3) |
From the CFC editor, try the option of CFC Read Back. This may solve the problem for a single cfc uploading. Raheel. |