Good Morning. our plc has stopped communicating with ncu on the operating screen. NC / plc communication failure appears, on the electrical panel our plc has no number and a dot to the right. How do I reestablish this communication? ------------------------------------------------------------------------------------------ |
Last edited by: Jen_Moderator at: 12/03/2019 13:20:06New subject after splitting |
|
12/3/2019 12:31 PM | |
Joined: 4/23/2010 Last visit: 12/31/2023 Posts: 8092 Rating: (878)
|
Hello, Please create new topic instead of posting in old topic. You have not mentioned your controller type, but I presume it to be 840D. From your attached snap, it looks like NCU has detected error in cyclic operation. Please switch OFF & ON power of NCU & check if same status of NCU repeats. If so, check if you have valid NC/PLC start up data on your machine or on external storage devices. After confirmation of valid NC/PLC data, please clear NC/PLC data (refer attached sheet for details) & check NCU should display number 6. If it is so, then you can reload NC/PLC data. If there is no any change in NCU seven segment display, please remove PCMCIA card from its slot & reinsert it & check. If problem persist, probably you need to check 840D NCU box. HTH. AttachmentNC-PLC_archive_clear_restore procedure.zip (232 Downloads) |
12/3/2019 1:07 PM | |
Joined: 12/3/2019 Last visit: 11/6/2024 Posts: 19 Rating: (0) |
We try to do the restore with NC, but when we hit start it starts to run and give error. follows attached. |