1/25/2022 7:43 PM | |
Joined: 8/12/2021 Last visit: 10/15/2024 Posts: 325 Rating: (30) |
Hi Nikhil017, You may find the following link helpful: SIMATIC S7-300 SM331; AI 8x12 Bit Getting Started part 1: 4 -20mA |
If this Information really helps, you could use the Rate function |
|
1/27/2022 7:33 AM | |
Joined: 10/7/2005 Last visit: 10/15/2024 Posts: 3024 Rating: (1054)
|
Correct
NO, these limits can be optionally set/used for Ch0 and Ch2 if limit hardware interrupts are enabled. The attached pic should provide clarity on both items. |
Cheers |
|
1/31/2022 4:44 AM | |
Joined: 10/7/2005 Last visit: 10/15/2024 Posts: 3024 Rating: (1054)
|
Hi Nikhil017 to start with, do yourself a favour and grab the COM PB manual from HERE as a general more than handy to have reference. Thereafter, have a look at page 35 and make sure the Analogue format is set to S7 format. Once done, realise that S7 Analogue format means that 4-20mA equates to 0-27648 and also see chapter 5.1 of THIS manual for more. |
Cheers |
|