9/16/2025 1:24 PM | |
Joined: 8/3/2009 Last visit: 9/16/2025 Posts: 16436 Rating:
|
Hello rhsb If this are alarms from PLC (also Diagnostic) then the text comes also from the PLC in Runtime. For this the used Runtime language has to be loaded also in the PLC. I think its the same as for the Clasic Panels: https://support.industry.siemens.com/cs/de/en/view/109759021 So check which Languages you have loaded in the PLC (notice that a S7-1500 can only load 3 languages at the same time) Bye Murof |