11/12/2013 11:01 AM | |
Joined: 8/25/2006 Last visit: 8/7/2024 Posts: 2207 Rating:
|
Hello. Did you try to set checkbox 'Initial load' when downloading?Checkbox "Initial load" while downloading a D7-SYS program Try to download by the following method: T400 problems with downloading the configured software (application software): If a new program cannot be downloaded into a T400 (downloading is interrupted with the message "CPU does not respond”): Set switch S1/7 on the T400 to ON (T400 then exclusively processes the download program); then re-start downloading; If loading is completed: Set S1/7 back to OFF. |
11/12/2013 1:25 PM | |
Joined: 8/31/2005 Last visit: 7/18/2024 Posts: 2198 Rating:
|
Mark "initial load" bevor you start the download.
Which one?
In "initial load" is not marked the system compares theprojected namesof rack and CPU. If it is not identicalyou get the error. Follow chapter 5.4 in this manual. |
|
|
11/12/2013 2:32 PM | |
Joined: 8/31/2005 Last visit: 7/18/2024 Posts: 2198 Rating:
|
Try to set the COMx settings in the system panel to "9600,9,n,1,no fow control" in the extended parameters try it withactivated FIFO and without FIFO. Use the checkbox to deactivate/activateit) Which operating systemdo you use on your PC? Do you have a built in COM port or a USB-serial converter? AttachmentD:\COMx.zip (598 Downloads) |
|
|
11/12/2013 2:37 PM | |
Joined: 8/25/2006 Last visit: 8/7/2024 Posts: 2207 Rating:
|
|
Follow us on