8/14/2018 11:00 AM | |
Joined: 10/11/2006 Last visit: 6/5/2024 Posts: 5857 Rating: (793)
|
Hello, if motor cable and resolver cable is checked (connect the motor in U/V/W), you can do a position test function for the rotor position (see chapter 7.3.4 in the Masterdrives Compendium) If you find a wrong angle, the resolver is not in the original position as it left the factory. If this does not solve your problems, I would recommend to contact the Technical Support. |
With best regards, |
|
8/15/2018 11:01 AM | |
Joined: 3/2/2015 Last visit: 5/2/2024 Posts: 45 Rating: (0) |
We did check the angle using info from chapter 7.3.4 which displayed an error of less than 1% in all three lockup positions - all good. The problem turned out to be the non-execution of P115 being set to 2. Please refere to my previous SOLVED answer above. Thank you for your help anyway |