2/24/2025 12:32 PM | |
Joined: 4/24/2006 Last visit: 7/31/2025 Posts: 9027 Rating:
|
Hello, The module is based on 6ES7134-4GD00-0AB0 Here is a link to manual: SIMATIC ET 200S distributed I/O 4AI I 2WIRE ST analog electronic module (6ES7134-4GD00-0AB0) See paragraph 1.1 for wire connection. It is a 2-wire card, that means you have a Passive sensor? The card supplies the power to generate the mA. Or do you have an Active sensor, the supply of the sensor is from another powersupply, Then you need a 4-wire card. (6ES7134-4GB11-0AB0, see manual 2AI I 4WIRE ST analog electronic module (6ES7134-4GB11-0AB0) (See paragraph 1.1 for wire connection) Best regards, Wizard |
Last edited by: Wizard at: 02/24/2025 12:39:18 |
|
2/24/2025 4:18 PM | |
Joined: 3/31/2018 Last visit: 6/28/2025 Posts: 36 Rating:
|
Hi, the transmitter is passive |
2/25/2025 11:19 AM | |
Joined: 3/31/2018 Last visit: 6/28/2025 Posts: 36 Rating:
|
|
2/25/2025 11:20 AM | |
Joined: 3/31/2018 Last visit: 6/28/2025 Posts: 36 Rating:
|
|
2/25/2025 11:20 AM | |
Joined: 3/31/2018 Last visit: 6/28/2025 Posts: 36 Rating:
|
|
2/25/2025 11:51 AM | |
Joined: 3/31/2018 Last visit: 6/28/2025 Posts: 36 Rating:
|
Hi, First time hearing, what is Process Image? Could you please tell in detail? |
2/25/2025 12:37 PM | |
Joined: 4/24/2006 Last visit: 7/31/2025 Posts: 9027 Rating:
|
Hi, The CPU reads every cycle the Process Image. And put it in a table, to be used in the program. Go to properties of CPU151-8, -> Cycle Here you will find the Size of Process Image Input and output. Those addresses are read every cycle. But when your address is outside this Process Image, you will need to read it through PIW, it will go to your card and get the value of the address. Perhaps this link might help:Where and when do you need peripheral addressing? This is for S7-300/ S7-400 CPU's Best regards, Wizard |
This contribution was helpful to
2 thankful Users |