Joined: 3/11/2019 Last visit: 9/1/2025 Posts: 1653 Rating:
|
Hi, You have to use the input/channel somewhere in the safety program, otherwise the status will not be updated. Means, if you only install the hardware and monitor the input in the tag table, nothwing will be shown! The input/channel must be used in the safety program! (not standard program). Is this the case? Why does the status of fail-safe inputs and outputs not change in the watch (monitoring) table?regards sancruz |
Last edited by: sancruz at: 06/13/2024 11:16:23Feedback appreciated, please rate |
|
6/24/2024 11:09 AM | |
Posts: 10 Rating:
|
Thank you very much for the information! I have tried how you said and it works. best regardds, issam |