Hello Jabi.
For physical connection, I recommend a profinet cable connecting the PLC and the IOT. Pay attention to the IP adresses of the PLC and the IOT:. |
3/19/2017 3:05 PM | |
Posts: 14 Rating: (0) |
你好, 我的CPU为1516-3 PN / DP(6ES7516-3AN00-0AB0),不能更新到固件V2.0。 是不是意味着我不能在TIA-PortalV14中使用OPCUA? 所以可以告诉我另一种方式来建立这个CPU和IOT2040? 最好的祝福 Jabi |
3/20/2017 9:57 AM | |
Joined: 4/28/2015 Last visit: 11/12/2024 Posts: 3345 Rating: (379)
|
Yes this is correct. The OPC UA Server of the S7-1500 CPUs is only supported with Firmware 2.0 and TIA Portal V14. For example you can use S7 connection with node-red. How to use is described in this application example. Best regards! |
Not working for IOT2050 support anymore from March 1st, 2024. |
|
3/20/2017 9:59 AM | |
Posts: 215 Rating: (6) |
Unfortunately, the PLC you have is not able to be updated to Firmware 2.0 (as seen here). This is due to the hardware inside your PLC. Newer versions have newer hardware, which is able to use Firmware 2.0. You could use S7 communication. Here is an example on how to do so. |