7/1/2024 7:11 AM | |
Joined: 6/23/2008 Last visit: 10/24/2024 Posts: 1168 Rating: (283)
|
Hello Simocode pro V PN supports the system redundancy S2 and hence can be used in combination with a redundant PLC (H-System). But Sinamics G120 (PN-versions of Control Units) actually (7/2024) do not support system redundancy S2 and can't be used with a redundant PLC. To be more precisely, you could etablish the communication to only one CPU of the redundant pair with G120 PN-Control Units, means the communication will get lost in case this CPU fails. Usually this is not, what most users want to archieve. For redundant connection of G120 to an H-System, you need to use Profibus version of Control Unit in combination with Y-Link. You need to consider, that it is not only a question of physical connection when it comes to connecting a PN-IO-device to a H-System, but also a question of at least S2 capability (non redundant Profinet-network with H-System or after Y-switch or R1-capability (direct connection to redundant Profinet-network). See here: https://support.industry.siemens.com/cs/de/de/view/109747976/en Best regards... |
"Expert" does not necessarily mean Siemens employee. Please cross-check your requirements always with official Siemens documentation. Also "Experts" are pleased about feedback. Please don't send support requests as PM. Questioners who don't follow up their thread will be put to my list of users to be ignored. |
|
This contribution was helpful to1 thankful Users |