8/30/2024 5:06 AM | |
Joined: 3/11/2019 Last visit: 9/1/2025 Posts: 1653 Rating:
|
Hi again, of course you can use BaseUnit A0 with thermocouples! But as described in the other post, you can not use the "internal reference junction" for compensation (which is recommended). So if you use the A0, you need another reference like an additional PT100. I am a bit confused to be onest, because everything is described in the FAQ already posted in the old post. In the FAQ additional links to the other compensation methods are available. What do you have to watch out for when using thermocouples if the expected value is not displayed?So the bottom line is:
regards sancruz |
Last edited by: sancruz at: 08/30/2024 05:14:20Feedback appreciated, please rate |
|
This contribution was helpful to
1 thankful Users |
Follow us on