Dear Radnuss, If you want to keep the air below 75°C than I would recommend the application A07 from the RLU220, RLU210 is no more in sale. Send you as attachment the application sheet of the application A07, the basic documentation and other document can be found in HIT. https://hit.sbt.siemens.com/ Hope this help Best regards RichardF Attachment50571_Supply air temperature control_en.doc (164 Downloads) |