Hello Rasalcce; Robster's information is correct. As you can find in the attached datasheet (from the Industry Mall), the PAC3200 communicate either over SEAbus TCP or Modbus TCP. Here you can find information on the S7 Modbus TCP interface "Open Modbus TCP"; check that you download the package for the integrated PN interface of yoiur CPU, if that is what you want to work with. Look also at downloading the Modbus TCP wizard for your application, it is also available in the link mentionned. It will make your life easier for programming the exchanges. http://support.automation.siemens.com/WW/view/en/22660304 You can dowload the demo version of the software here: www.siemens.com/s7modbus Hope this helps, Daniel Chartier AttachmentDatasheetService_PAC3200.pdf (1077 Downloads) |
Last edited by: dchartier at: 8/27/2010 5:50 PMLast edited by: dchartier at: 8/26/2010 2:49 PM |
|