hi everyone, i am also facing same problem with SIMIT v10.2. is there any way to import DB address into SIMIT? |
6/14/2024 8:46 AM | |
Joined: 2/1/2021 Last visit: 9/30/2024 Posts: 1430 Rating: (143)
|
Hello Forum Community, hello Bjarne__De_Smedt, hello Palrajinder, With PLCSIM DB import from S7-300/400 in SIMIT is not possible. For having DB import you can use Virtual Controller instead of PLCSIM. See SIMIT V11.2 manual, p. 153 for further information. When you use a S7-1500 controller the software PLCSIM Advanced and a user-defined coupling in SIMIT can be used to access data blocks. You can contact your regional technical support team. The regional colleagues can provide you with the user-defined coupling and help you with implementation and use: An overview of other SIMIT couplings can be found here: SIMIT couplings, applicative extensions of the interface - ID: 109795246 - Industry Support Siemens The procedure for integrating an external coupling is described here: Yours sincerely, SIMATIC-FB-Allgemein-GER (MS, VB) |
6/21/2024 8:39 AM | |
Joined: 6/19/2017 Last visit: 9/6/2024 Posts: 8175 Rating: (172) |
New question published by TechMicke is split to a separate thread with the subject SIMIT - Data Block import S7-1500. Best regards |