Hi, the drives exchanges "standard" data (IW QW) with the CPU (name as profidrive telegrams). You can choose different "telegrams", e.g. telegram1 is the simplest. The CU manual descript the meaning of each bit in the telegram, but e.g. telegram 1 has always same meaning: 1 control word, 1 speed reference 1 status word, 1 current value. you can manually set the bit/word values (e.g. control word = 47F = RUN, 47E = STOP, HEX 400 = 100% of speed) or use some ready for use block to do it for you (like SINA_SPEED). |