11/8/2019 8:37 AM | |
Posts: 2 Rating: (0) |
Hi, How do I codify the error code displayed in S7 400 H CPU Diagnostic Buffer. Regards Vijay ------------------------------------------------------------------------------------------ |
Last edited by: Jen_Moderator at: 11/08/2019 10:52:27New subject after splitting |
|
11/8/2020 12:09 PM | |
Posts: 2 Rating: (0) |
Hi, To decode the hex code printed in the CPU Diagnostic buffer one should relate these codes with respective error OB and its Temp Variables. Ex. Message in CPU Diagnostic Buffer is - 16# 3942 1952 D054 00E0 0D15 0000 then decoding of this Hex code is as below - 16#39 - OB82_EV_CLASS 16#42 - OB82_FLT_ID 16#19 - OB82_PRIORITY 16#52 - OB82_OB_NUMBR 16#D0 - OB82_RESERVED_1 16#54 - OB82_IO_FLAG 16#00E0 - OB82_MDL_ADDR 16#0D - Total 8 Bits - OB82_MDL_DEFECT, OB82_INT_FAULT, OB82_EXT_FAULT, OB82_PNT_INFO, OB82_EXT_VOLTAGE, OB82_FLD_CONNCTR, OB82_NO_CONFIG and OB82_CONFIG_ERR 16#15 - OB82_MDL_TYPE - Bit 0 to Bit 7 16# 0000 - Total 16 Bits - OB82_SUB_MDL_ERR, OB82_COMM_FAULT, OB82_MDL_STOP, OB82_WTCH_DOG_FLT, OB82_INT_PS_FLT, OB82_PRIM_BATT_FLT,, OB82_BCKUP_BATT_FLT, OB82_RESERVED_2, OB82_RACK_FLT, OB82_PROC_FLT, OB82_EPROM_FLT, OB82_RAM_FLT, OB82_ADU_FLT, OB82_FUSE_FLT, OB82_HW_INTR_FLT and OB82_RESERVED_3 Vijay Kulkarni |
11/15/2020 8:21 AM | |
Joined: 12/10/2018 Last visit: 6/27/2024 Posts: 109 Rating: (11) |
Hello dear friend You can find the meaning of diagnosticj interrupt in below document. Attachments7wsvhdb_en-US.pdf (639 Downloads) |
Follow us on