Hi At first please take alook at S7-400H SIMATIC Fault-tolerant systems manual,chapter 13 (use i/o s in s7-400h), section 13.4 ( connecting redundant i/o to profibus interface) , page 177( using blocks) for detail information. Also you will find this: "To be able to address redundant modules using process image partitions in cyclic interrupts, the relevant process image partition must be assigned to this pair of modules and to the cyclic interrupt. Call FB 450 "RED_IN" in this cyclic interrupt before you call the user program. Call FB 451 "RED_OUT" in this cyclic interrupt after you call the user program. The valid values that can be processed by the user program are always located at the lower address of both redundant modules. This means that only the lower address can be used for the application; the values of the higher address are not relevant for the application." So you must use the lower address. Hope this helps Regards hosein
|