10/17/2019 8:13 AM | |
Joined: 7/27/2017 Last visit: 7/25/2024 Posts: 79 Rating:
|
My potentiometer is connected at x174, 4, but the % I don't know which parameter to set that. |
10/17/2019 8:34 AM | |
Joined: 4/23/2010 Last visit: 11/23/2024 Posts: 8092 Rating:
|
Hello nanchi, Have you checked filed current when start/enable command is applied? Is it rated motor field current? Please check set point value as suggested by expert KSN in earlier post. Furthermore, check set point potentiometer wiring connections. |
10/22/2019 5:32 AM | |
Joined: 8/25/2006 Last visit: 9/17/2025 Posts: 2218 Rating:
|
Hello. If the electronics power supply (5U1, 5W1, 5N1) is disconnected when the machine is running there will be the fault F001 (Failure of electronics power supply). If the electronics power supply is disconnected with any active fault< then after restoring power supply there will be fault F040 (Electronics supply disconnected in active fault status). Look at the manual and this FAQ. |
This contribution was helpful to
1 thankful Users |