4/5/2024 1:58 PM | |
Joined: 10/11/2006 Last visit: 1/10/2025 Posts: 5980 Rating: (823)
|
Hello M2024, you can use macros of V20 to set up the parameters to use V20 in predefined setups. You can also use this predefined settings and adapt them according to your needs. See section 5.5.1.3 of V20 operating instruction manual, i.e. macro Cn002. https://support.industry.siemens.com/cs/ww/en/view/109824500 |
With best regards, |
|
4/26/2024 10:15 AM | |
Joined: 2/12/2024 Last visit: 12/5/2024 Posts: 7 Rating: (0) |
But it should work without using USS if I'm just sending wired voltage from the plc right? |
4/30/2024 9:15 AM | |
Joined: 2/12/2024 Last visit: 12/5/2024 Posts: 7 Rating: (0) |
IT works ! we should configure P0757 To P0761 and P2000 properly. |