2/1/2017 7:46 AM | |
Joined: 11/12/2006 Last visit: 11/9/2021 Posts: 33 Rating: (0) |
Hi Christoph, I just tried what you suggested with my CPU 315. On the Online menu the "Upload device to PG/PC..." is greyed out and can't be selected. See attached screenshot. The PLC was configured with the same version of TIA Portal. Thanks Ross Umbers Attachmentscreenshot.pdf (381 Downloads) |
2/1/2017 7:53 AM | |
Joined: 5/12/2006 Last visit: 9/3/2024 Posts: 22352 Rating: (3008)
|
Hello, which FW Version have the PLC? If the FW <V2.6 then TIA can't upload because this PLC is only supported with FW V2.6 in Tia. https://support.industry.siemens.com/cs/ww/en/view/97554052 You can also try to create a offline configuration with this PLC Type and backup the Online Config, like described in the FAQ. The Option "Upload as new Station" was available since V13, so is not available in you V12 version.
Christoph |
Last edited by: ChristophD at: 2/1/2017 8:11:55 AMLast edited by: ChristophD at: 2/1/2017 8:12:43 AMLast edited by: ChristophD at: 2/1/2017 8:15:55 AM |
|
3/8/2024 5:33 PM | ||||
Joined: 12/14/2017 Last visit: 4/10/2024 Posts: 7 Rating: (0) |
If I do this, will all of the network comments and interface labels be kept, or will they be deleted? |
|||
3/8/2024 5:35 PM | |
Joined: 5/12/2006 Last visit: 9/3/2024 Posts: 22352 Rating: (3008)
|
this depend on the PLC you use S7-300 do not save such informations in the PLC. |